Revit2010 MEP "Check Duct Systems" error... HELP!


erratic

Recommended Posts

It is not possible to calculate the flow since all the components in this system have the flow configuration set to Preset or System. At least one component is required to have the flow configuration set to Calculated

 

Anyone else come across this error message - and if so, how did you solve it? I cannot seem to find where to adjust this... any guidance is appreciated!

 

Thanks!

8)

Link to comment
Share on other sites

  • 4 weeks later...

Your diffusers need to be set to calculated. Enter in the values for each diffuser and your systems should populate with the pressure/flow info.