erratic Posted March 31, 2010 Posted March 31, 2010 It is not possible to calculate the flow since all the components in this system have the flow configuration set to Preset or System. At least one component is required to have the flow configuration set to Calculated Anyone else come across this error message - and if so, how did you solve it? I cannot seem to find where to adjust this... any guidance is appreciated! Thanks! Quote
Methuselah Posted April 28, 2010 Posted April 28, 2010 Your diffusers need to be set to calculated. Enter in the values for each diffuser and your systems should populate with the pressure/flow info. Quote